[PLUG] Re: UPS failure/replacement
Russell Senior
seniorr at aracnet.com
Sun Dec 18 05:33:47 UTC 2005
>>>>> "Aaron" == Aaron Burt <aaron at bavariati.org> writes:
Russell> How much voltage should there be on a dead battery? I just
Russell> measured 13.15 and 13.2 V, respectively. PowerSonic PS-12120
Russell> F2.
Aaron> Looks OK, though often a bad battery can show a good voltage,
Aaron> but fail a load test. Short the battery for a half-second with
Aaron> a long piece of wire and then measure the voltage. Or see if
Aaron> you can monitor the battery voltage during a UPS test. Or you
Aaron> could put the UPS into Runtime Calibration mode.
Well, it had enough juice to cook a 47 ohm resistor in about 5 seconds
with no measurable loss of voltage. My guess is that batteries are
okay.
--